Connection help Nilan VP18cCom #57
-
Hi, I am new on Home assistant and i have a nilan device in my home, a VP18cComp with a MODBUS LAN interface from Nilan Type 238481 (ES1140). I try to connect after installing HACS and your github repository but with no result for now. So i have 2 questions : What is the device name ? The modbus id ? My version oh HA: Return error: Connection to (hidden IP, 502) failed: timed out Many thanks for your help and your work !! |
Beta Was this translation helpful? Give feedback.
Replies: 2 comments 5 replies
-
Device name is what you like. Modbus id is by default 30, but you can see it in the HMI menu if it is something else. You can only find the modbus version by reading it via modbus. You can follow this #9 to find out the modbusversion from chart. Yours is 22 so the newest I know. |
Beta Was this translation helpful? Give feedback.
-
Hi, Thank you for your answer ! I took a look in the HMI service menu and the modbus is 30 indeed. Thanks, i understand so the modbus version is 22 because of the software version is 1.6.56.0. So, have you any idea about this return error ? I always have the same error : Connection to (hidden IP, 502) failed: timed out Ping to the IP is ok. If i understood well, your code support the modbus version 22, i understand well ? Thank you in advance for your help ! |
Beta Was this translation helpful? Give feedback.
Hi,
Thank you for your answer !
I took a look in the HMI service menu and the modbus is 30 indeed.
Thanks, i understand so the modbus version is 22 because of the software version is 1.6.56.0.
So, have you any idea about this return error ? I always have the same error : Connection to (hidden IP, 502) failed: timed out
Ping to the IP is ok.
If i understood well, your code support the modbus version 22, i understand well ?
Thank you in advance for your help !