how to config WCS1700 Hall-Sensor #76
-
Hello, how do i config WCS1700 Hall-Sensor in the config file. I reviewed the code from bettapro on github, but my lack of programming skills lead me to failure. that is what i modifyed and i think last part isn't right. The output on the virtual pin 12 a littel bit of.
|
Beta Was this translation helpful? Give feedback.
Replies: 2 comments 1 reply
-
You have to adjust these parameters according to the sensor you're using:
Default values are not correct for WCS1700 (3.3v supply):
Use the sensor datasheet as reference: https://www.winson.com.tw/uploads/images/WCS1700.pdf |
Beta Was this translation helpful? Give feedback.
-
hello bettapro, than you for your answer. So i have done something awaiting a hint. At first i measured aOut an got 1,59V@ no load on the system. Out of the datasheet i got 32mV for one ampere. my test parameter are
Is it right das the measured parameter is forwarded to pin V12 ? thx for your help |
Beta Was this translation helpful? Give feedback.
Seems resonable and close enought.
One side note: WCS1700 should measure current "to the load", the overall current (virtual pin 12) is calculated as:
current from SCC to the batteries - current of the loads ( measured by WCS1700)