Replies: 1 comment
-
This is not really normal, but it is typical, Daikin behavior. Must be something in the control loop for the LWT. If it occurs, it often means that the average LWT stays somewhat above the LWT setpoint, increasing the risk of an overshoot and an off/on cycle, so it is recommended to keep the overshoot setting [9-04] sufficiently high (as done). Often, the modulation stops when the LWT setpoint is temporarily increased by 1C which can be done with the offset value (in WD mode) or with the ABS value (in ABS mode). |
Beta Was this translation helpful? Give feedback.
0 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
-
It's my first season with a heat pump and I'm not sure if thats normal behavior. Maybe someone could share his experience.
My heat pump runs the whole day at a relativ constant rate, but there are micro power fluctuations with 200w.
Are these normal? Is it normal that it runs at such a constant rate? It seams to be very efficient, only consuming about 12kwh a day.
Outside conditions on this way are stable at 4-6°.
My current config:
Overshot 4, Modulation On, I have a Madoka installed, setpoint -1
Beta Was this translation helpful? Give feedback.